Robert Gift wrote:So, they BOTH cannot be conducting electricity simultaneously?
I can understand that if the front has moved to a new circuit while the back is still on the another.
Is the retracted pantograph NOT connected internally and therefore not charged?
Or is is still charged from the front voltage but simply cannot be raised
where it could cause a conflict?
When the AEM 7's were shipped from LaGrange, they had 1 MCB & 1 main transformer connected to it. On the pantograph side of the MCB was the pantograph selector knife switch (Front, Back, or Disconnected / Isolated) with safety interlocks to ensure Both pantographs were down before the switch could be operated (working off the batteries). Also on the pantograph side is the voltage detection circuit to ensure that the cantenary voltage matches the voltage that the operator has selected on the control stand (one at each end) selected to control the unit. If the voltage selected does not match what is on the wire, the incorrect tap connections do alot of damage to the unit if the MCB is allowed to connect to the incorrect cantenary voltage. The unit is designed so only one pantograph can be connected to the MCB. If I remember correctly, The main transformer had 6 taps, 1 for each traction motor, 1 for utilities, and 1 for HEP.
Each pantograph is raised or lowered at the discression of the operator. If the operator lowers the pantograph connected to the MCB, the MCB first opens then the pantograph is allowed to lower, then the unit drops to battery power (64 vdc).
I remember reading in a thread that the AEM 7's are operated with both pantographs up in clear weather. I don't understand why Amtrak subjects the cantenary & unused pantograph shoe to unnecessary wear.